I need a consultation, please. Here's the scoop:
I have an older, manual-start emergency generator, a Coleman rated at 5000 continuous watts. It got us through Irene and this latest outage, but not without problems. I've got it fully functional again after replacing the on-board circuit breakers, but it's not really quite large enough, plus there's no way my wife can start it if I'm not home. And the run time on a full tank is only about three hours. So -- I'm shopping for a new, electric-start generator.
What I'm finding is that the new ones all use a NEMA L14-30R (4-wire, twist-lock) receptacle. My existing one uses a NEMA 6-30R receptacle (3-wire, straight) and has an external grounding lug on the generator frame.
So I'll need to install a new L14-30R generator outlet. I know this has two hots, a neutral, and that the fourth wire is ground. I assume this means no external grounding lug on the generator. How do I wire the receptacle in the panel box? Do both the neutral and the ground get run to the neutral bus bar? If it makes a difference, my main breaker panel has no spares. There is a smaller, auxiliary panel (with no internal service disconnect) that has space for the new, 30-amp double breaker to which I'll be connecting the new receptacle.
If I decide to run conduit/EMT to the new outlet in an outer garage, what's the minimum size for four #10 conductors? If the generator is going to be approximately 30 feet (wire length) from the house panel, is #10 adequate or should I use #8 for voltage drop reasons? (I'll still be running through a 30-amp breaker.)
Thanks